ROOM2: INDR_T 0.6-0.7 °C above d50 never applied -> indoor sensor alarm

Shop › Forums › ThermIQ in english › General › ROOM2: INDR_T 0.6-0.7 °C above d50 never applied -> indoor sensor alarm

  • This topic is empty.
Viewing 1 post (of 1 total)
  • Author
    Posts
  • #8791
    danieldamdk
    Participant

    Thermia Diplomat G3, ThermIQ-ROOM2, sending INDR_T from a Shelly sensor via MQTT set (about every 5-30 min).

    Out of 35 sets since 15 Oct, all 4 with INDR_T – d50 = +0.6/+0.7 (23.6/23.7 with d50 = 23) were echoed by ROOM2 (INDR_T in /data), but never applied in the pump (r01/r02 unchanged). Exactly ~4.5 min later the pump raises the indoor sensor alarm (r14 bit 4) and falls back to 20.0 °C. All 31 other sets (from -2.4 to +0.4 and from +0.8 to +1.7 relative to d50) were applied within ~30 s.

    Only a ROOM2 power cycle clears the alarm (it then starts at 20.5 as documented); a new set does not. The old Thermia Online module is disconnected from EXT.

    1) Is this a known limitation of the room unit protocol (values just above the setpoint)?
    2) What does the MQTT command “reset” do: reboot or configuration reset?
    3) Is there a safe way to restart ROOM2 remotely?

    Thanks!